ENDEAVOR® 5-10KVA

ONLINE UNINTERRUPTIBLE POWER SUPPLY

2G-ED8-10kVA-BP-KTF-04

ENDEAVOR® 5-10KVA ONLINE UNINTERRUPTIBLE POWER SUPPLY

Double conversion rack/tower UPSs with LCD Display for critical IT, telecommunications, and security systems

The Minuteman® Endeavor 5-10kVA Series delivers uninterrupted power for vital IT, telecom, and security setups. With a clear LCD Display for instant updates on AC, battery, and UPS status, this UPS is generator-compatible, versatile, and ensures maximum uptime. Offering pure sine wave output and adaptability for critical applications, it’s the ultimate choice for reliability and efficiency.

APPLICATIONS

  • High-Density Installations
  • Enterprise Network Installations
  • Network Corporate Servers
  • Telecom/VoIP Systems
  • Extended Runtime

The Endeavor 5-10kVA is a high-density, double-conversion online UPS series providing unparalleled power protection for critical IT and business infrastructure. With a unique multi-color touchscreen panel for easy management and monitoring, this UPS offers a wide range of installation options and is ideal for servers, networks, industrial applications. The Endeavor 5-10kVA has advanced features like predictive battery replacement and hot-swappable batteries, it’s designed for IT professionals and administrators needing reliable power solutions.

New Advanced Features

  • Multi-color, touchscreen LCD panel for easy UPS configuration and monitoring
  • Compact design: 4U for 5/6kVA, 5U for 8/10kVA (208VAC models)
  • High-frequency design for efficient performance
  • Space-saving solution for higher density installations
  • Predictive Battery Replacement feature with early warning alarms
  • Tool-less, front-panel battery connection and replacement
  • Hot-swappable batteries for continuous power
  • Independent battery chargers for unlimited runtime
  • Automatic recognition of additional battery packs for recalculating runtimes
  • Easy connect transformer module with NEMA input plug
  • Wide range of 120V and 208V NEMA output receptacles available in standard configurations
  • Smart ECO Mode feature allows for increased energy savings

Key Features & User Benefits

  • True double-conversion online technology: Provides maximum protection for critical equipment.
  • Digital Signal Processor (DSP) design: Enhances reliability by reducing the number of UPS components, ensuring robust performance.
  • High power factor (0.9pf): Increases real power capacity for each model, delivering more reliable power to connected devices.
  • 120/208V output models with standard receptacles: Offers flexibility to support multiple voltages used on connected loads.
  • Multi-function, color LCD touchscreen display: Enables full UPS configuration and real-time monitoring of input/output power and load condition for user convenience.
  • User-configurable voltages (208V as default): Greater flexibility in tailoring the UPS to suit diverse environments.
  • Automatic internal bypass: Activates Bypass Mode and alerts users in the event of hardware or battery faults, ensuring continuous power.
  • Independent Battery Bypass (IBB): Maintains constant 120/208V output even with dead batteries when utility power is available.
  • Smart fan control: Maximizes UPS cooling efficiency with variable-speed fan control for optimal performance.
  • Cold start function: Start the UPS without available utility power, ensuring continuous operation.
  • Available option slot: Facilitates the use of network or programmable relay cards for enhanced functionalities.
  • Simultaneous serial communication options (USB and RS-232): Offers flexibility in managing and monitoring the UPS system simultaneously.
  • REPO Port: Supports immediate shutdown of output power in emergency situations for added safety.
  • 3-year standard product warranty: Reduces ownership costs and assures greater reliability.
  • Optional 5-year warranty options available: Provides peace of mind with extended guarantees for up to 5 years.
  • Platinum Protection Plan®: Insures connected equipment for up to $250,000, ensuring comprehensive protection.
  • RoHS2 and Energy Star 2.0 compliant: Environmentally-friendly design reduces operating costs and ensures energy efficiency.

LCD Status Panel

Multi-colored Touchscreen LCD Display Panel offers all these features and more:

  • User-friendly UPS configuration and status display
  • Clear and descriptive UPS status information in plain text
  • Convenient display of UPS Serial Number and Model Number
  • Display of Battery Module part number and FW number for easy identification
  • Front screen adjustment for input voltage transfer points and sensitivity
  • Output voltage adjustment accessible via the front screen
  • Serial number reporting through software and SNMP card
  • Easily set Battery Replacement date and manage External Battery Packs from the front screen
  • Access Event logs (Faults & Warnings) directly via the front screen
  • Control Load Shedding function and reset settings to factory defaults via the front panel
  • Display load capacity per output bank and total load for quick assessment
  • Check load bank state and reset Battery Aging Coefficient using the front panel controls

The LCD panel is designed so that it can be oriented vertically or horizontally depending on the installation orientation of the UPS.

Electrical Characteristics

Digital Signal Processor

  • Reduced number of components in the UPS also reduces the potential for defects or malfunctions
  • Digital Signal Processor, (DSP), combines many components into a single processor, increasing the reliability of the UPS and reducing any downtime potential
  • Helps ensure stable, quality power and long life span

High Output Power Factor

  • All models feature an output power factor of 0.9 which increases the Watt capacity of the units
  • Larger capacities in a smaller UPS VA rating can reduce the overall cost of the UPS solution for a specific load requirement

Output T.H.D.

  • Endeavor units maintain an output AC signal within 2% of a true sine wave pattern (Total Harmonic Distortion)
  • Prevents equipment damage from internal heat build up on sensitive connected equipment

Overload Capacity

  • Endeavor UPSs are designed to support such situations with the ability to absorb up to 150% of its rated load for up to 30 seconds
  • Allows the UPS to be sized for maximum capacity without worry of overload and shutdown, providing cost-savings

Advanced Battery Features

  • Independent Battery Bypass allows the Endeavor UPS to operate in Normal Mode, even with weak, dead, or defective batteries
  • Endeavor UPSs monitor internal battery status at regular intervals; If the UPS detects weak or bad batteries, it will engage an audio alarm and also any preconfigured electronic notifications
  • Normal AC output will be maintained as long as utility power is supplied within the UPS’ nominal input range
  • The UPS will have a constant 120/208/240V signal and protection from any dangerous spikes or surges while allowing time to replace batteries without having to shut down connected equipment

Optional 240V Output

  • Endeavor units can be configured for use with 220, 230 and 240V input and output.
  • For information about additional configuration options, please contact your Minuteman representative.

Communication Features

Bundled with SentryHD software

  • Minuteman SentryHD auto-shutdown and monitoring software is available for free download.

SNMP-compatible (SNMP-NV6 card)

  • All models include a standard internal communication slot which is compatible with all current Minuteman SNMP card options
  • Adding an SNMP-NV6 card allows remote management and control over any IP-based network
  • The Option card slot and serial communications port can be operated simultaneously, allowing SNMP to be used in conjunction with Minuteman SentryHD software

Battery Technology

Extended Runtime Capability

  • All models come with internal batteries standard.
  • For protection through extended blackouts, the Endeavor Series can daisy-chain multiple battery packs, providing unlimited runtime capabilities.

External Battery Pack Chargers

  • Independent battery pack chargers are a standard feature for applications that require extreme runtimes and multiple battery packs.
  • These chargers can shorten the recharge time of all the connected battery packs exponentially.
  • Critical for installation environments that experience frequent outages or long periodic outages.
Battery Technology

  • All Endeavor 5-10kVA units and battery packs use valve-regulated lead-acid batteries (VRLA); safe for all freight transport
  • For added protection, all models ship with batteries disconnected.
  • A Quick Installation Guide is included with each unit to detail how to connect the batteries before startup

Hot-Swappable Batteries

  • Batteries in the UPS and Battery Packs can be removed and replaced through the front panel, without the need to shut down the UPS.
  • Because batteries can be replaced while the UPS is operating in Normal Mode, connected loads are protected from voltage anomalies and spikes and surges while the batteries are being replaced.
  • Batteries are accessible and removable without the use of any tools.

WARNING: This product can expose you to chemicals, including Nickel, which are known to the State of California to cause cancer and birth defects or other reproductive harm. For more information, go to: www.P65warnings.ca.gov/product

Software

Get ultimate control over your power with SentryHD

In today’s complex world of data, networks, and software, control and management of applications is vital, especially when it comes to the power that is supplied to these devices.

SentryHD, included free with all current Minuteman UPS systems, is the latest update to Minuteman’s popular Sentry monitoring and management software. This powerful tool provides users and network managers a range of monitoring & managment tools for their power, allowing total control before, during, and after power problems.

With a simple connection to the UPS via USB or RS-232, SentryHD provides the capability to configure UPSs, monitor power, and diagnose issues, all from secure connections on the network. This eliminates wasteful runs around the facility, saving time and money.

Accessories

External Maintenance Bypass

  • ED-MTBS-10K

 


Battery Pack Models

Because each UPS has different battery requirements to support its maximum load capacity, the Endeavor 5-10kVA Series uses battery packs sized to match each UPS model.

External Battery Packs for Extended Runtime

  • BP192V5CRTXL (5 & 6kVA)
  • BP192V10CRTXL (8 & 10kVA)
  • An optional external battery pack is available for applications that require extended runtimes (5 or more external battery packs)
  • These battery packs include internal chargers that can shorten the recharge time of all the connected battery packs exponentially
  • Critical for installation environments that experience frequent outages or long periodic outages

 


Power Management via SNMP Communication

Optional SNMP-NV6 network card allows for easy management of UPS without the need for a connected PC or server

  • SNMP-NV6

Optional Programmable Relay Card:

  • Monitors UPS events
  • 6 programmable relay output contacts
  • Configurable normal open or normal close for each relay contact
  • Configurable UPS shutdown delay time
  • Configurable input signal as shutdown UPS or battery test
  • Has the ability to protect up to 6 computers unattended shutdown gracefully

WARNING: This product can expose you to chemicals, including Nickel, which are known to the State of California to cause cancer and birth defects or other reproductive harm. For more information, go to: www.P65warnings.ca.gov/product

Extended Warranty Plan

5 Full Years of Trouble-free Service – Guaranteed

Minuteman UPSs already ship with the best warranty in the business at 3 years, including non-prorated battery coverage on most products.

Two levels of Extended Warranty Plans are also available on most UPS product lines to provide an additional 2 years of coverage. These plans ensure a full 5 years of trouble-free ownership.

For complete product information, brochures and manuals visit out Resource Library.

Base Models
ED5KRT
ED6KRT
ED8KRT
ED10KRT
General Features
Topology
Double-conversion, Online
Number of Phases
Single (1ф 2W + G)
VA Rating
5,000VA
6,000VA
8,000VA
10,000VA
Load Capacity
4,500 Watts
5,400 Watts
7,200 Watts
9,000 Watts
Output Receptacles
(3) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
(3) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
(4) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
(4) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
Installation Format(s)
Rack or Tower
Input
Nominal Voltages
208 (Default), 220, 230, 240VAC
Acceptable Input Voltage
0 - 300VAC
Voltage Range
156-280VAC
180-280VAC
Power Factor Correction (PFC)
≥99% at Full Load
Frequency Range
40 to 70Hz at Full Load
Input Plug Type (Cord Length)
Hardwire w/optional NEMA L6-30P (6-ft.)
Hardwire only
Input Surge Protection
Resettable Circuit Breaker
Maximum Input Current
32 Amps
38 Amps
51 Amps
63 Amps
Surge Joule Rating
3,140 Joules 
Output (AC Normal)
Voltage Range
208 (Default), 220, 230, 240VAC
Voltage Regulation
208,220,230,240VAC (±2%)
Frequency Range
50/60Hz, auto selecting, +/-3Hz (unless synchronized to utility)
Efficiency (AC-AC)
93% at full-rated non-linear load
Output (Battery)
Output Waveform (Battery Mode)
True Sine-wave
Nominal Voltages
208 (Default), 220, 230, 240VAC
Voltage Regulation
Nominal +/-0.1% (until Low Battery warning)
Frequency Range
50/60Hz, +/-0.1Hz
Voltage T.H.D.
≤2% (Linear Load)
Overload Capacity
≥106% - ≤110% for 10 minutes / ≥111% - ≤125% for 5 minutes / ≥126% - ≤150% for 30 seconds
Batteries
Replacement Module
BM0097
BM0098
Tool-less Replacement
Yes (Front panel replacement)
Runtime (Full/Half Load)
3 min. / 11 min.
2 min. / 7 min.
3 min. / 11 min.
2 min. / 7 min.
Ind. Battery Bypass
Yes
DC Startup
Yes
Hot-swappable Batteries
Yes
Display & Communications
Front Panel Display
Multi-color, Touchscreen LCD
Alarm Silencer
Yes
Shutdown Software
SentryHD (available via download)
Communication Port(s)
USB/RS232 (Simultaneous access)
Comm. Cables Included
Yes
Remote Emergency Power Off Port
Yes
Environmental
Operating Temperature Range
+32° to +104°F  (0° to +40°C)
Storage Temperature Range
+5° to +131°F  (-15° to +55°C)
Operating (Storage) Humidity Range
0 to 95%, non-condensing
Operating Elevation
0 to +15,000 ft. (0 to +3,000m)
Storage Elevation
0 to +50,000 ft. (0 to +15,000m)
Physical
Unit Dimensions (L x W x H)
23.27" x 17.24" x 6.81" (591*438*173 mm)
28.74" x 17.24" x 8.54" (730*438*217 mm)
Shipping Dimensions (L x W x H)
36.0" x 36.0" x 18.8" (915*915*478 mm)
36.0" x 36.0" x 20.6" (915*915*95 mm)
Unit Weight
122.32 lbs. (55.5 Kgs.)
170.81 lbs. (77.5 Kgs.)
Add New
Shipping Weight
160.0 lbs. (72.6 Kgs.)
209.0 lbs. (94.8 Kgs.)
Warranty & Certifications
Standard Warranty
3 Years (Electronics and Batteries)
Connected Equipment Guarantee
$250,000
Safety Agency Approvals
cUL, CE
Certifications
UL1778, FCC Class B, Energy Star 2.0, RoHS2

Endeavor 5kVA and Transformers

UPS Model
ED5KRT-3KTF
ED5KRT-5KTF
General Features
Topology
Double-conversion, Online
Number of Phases
Single (1ф 2W + G)
VA Rating
5,000VA
Load Capacity
4,365 Watts
4,275 Watts
Output Receptacles (208-240VAC)
(2) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
(2) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
Output Receptacles (120VAC)
(8) 5-15/20R
(4) 5-15/20R / (2) L5-30R / (1) 3-wire Terminal Block
Installation Format(s)
Rack or Tower
Input
Nominal Voltages
208VAC (Default), 220, 230, 240VAC
Acceptable Input Voltage
0 - 300VAC
Voltage Range
156-280VAC
Power Factor Correction (PFC)
≥99% at Full Load
Frequency Range
40 to 70Hz at Full Load
Input Plug Type (Cord Length)
Hardwire w/optional NEMA L6-30P (6-ft.)
Input Surge Protection
Resettable Circuit Breaker
Maximum Input Current
32 Amps
Surge Joule Rating
3,140 Joules
Output (AC Normal)
Voltage Range
208VAC (Default), 220, 230, 240VAC / 120VAC (Default), 110, 115VAC
Voltage Regulation
110, 115, 120, 208, 220, 230, 240VAC (±2%)
Frequency Range
50/60Hz, auto selecting, ±3Hz (unless synchronized to utility)
Efficiency (AC-AC)
93% at full-rated non-linear load
Output (Battery)
Output Waveform (Battery Mode)
True Sine-wave
Nominal Voltages
208VAC (Default), 220, 230, 240VAC / 120VAC (Default), 110, 115VAC
Voltage Regulation
Nominal +/-0.1% (until Low Battery warning)
Frequency Range
50/60Hz, +/-0.1Hz
Voltage T.H.D.
≤2% (Linear Load)
Overload Capacity
≥106% - ≤110% for 10 minutes / ≥111% - ≤125% for 5 minutes / ≥126% - ≤150% for 30 seconds
Batteries
Replacement Module
BM0097
Tool-less Replacement
Yes (Front panel replacement)
Runtime (Full/Half Load)
3 min. / 11 min.
Ind. Battery Bypass
Yes
DC Startup
Yes
Hot-swappable Batteries
Yes
Display & Communications
Front Panel Display
Multi-color, Touchscreen LCD
Alarm Silencer
Yes
Shutdown Software
SentryHD (available via download)
Communication Port(s)
USB/RS232 (Simultaneous access)
Comm. Cables Included
Yes
Remote Emergency Power Off Port
Yes
Environmental
Operating Temperature Range
+32° to +104°F (0° to +40°C)
Storage Temperature Range
+5° to +131°F (-15° to +55°C)
Operating (Storage) Humidity Range
0 to 95%, non-condensing
Operating Elevation
0 to +15,000 ft. (0 to +3,000m)
Storage Elevation
0 to +50,000 ft. (0 to +15,000m)
Physical
Unit Dimensions (L x W x H)
23.82" x 17.24" 10.22" (605*438*260 mm)
23.82" x 17.24" 10.22" (605*438*173 mm)
Shipping Dimensions (L x W x H)
36.0" x 36.0" x 28.3" (915*915*719 mm)
36.0" x 36.0" x 28.3" (915*915*719 mm)
Unit Weight
210.48 lbs. (95.5 Kgs.)
243.54 lbs. (110.5 Kgs.)
Shipping Weight
262.0 lbs. (118.9 Kgs.)
295.0 lbs. (133.8 Kgs.)
Warranty & Certifications
Standard Warranty
3 Years (Electronics and Batteries)
Connected Equipment Guarantee
$250,000
Safety Agency Approvals
cUL, CE
Certifications
UL1778, FCC Class B, RoHS2

Endeavor 6kVA and Transformers

UPS Model
ED6KRT-3KTF
ED6KRT-5KTF
ED6KRT-6KTF2
General Features
Topology
Double-conversion, Online
Number of Phases
Single (1ф 2W + G)
VA Rating
6,000VA
Load Capacity
5,265 Watts
5,175 Watts
5,130 Watts
Output Receptacles (208-240VAC)
(2) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
Output Receptacles (120VAC)
(8) 5-15/20R
(4) 5-15/20R / (2) L5-30R / (1) 3-wire Terminal Block
(16) 5-15/20R
Installation Format(s)
Rack or Tower
Input
Nominal Voltages
208 (Default), 220, 230, 240VAC
Acceptable Input Voltage
0 - 300VAC
Voltage Range
156-280VAC
Power Factor Correction (PFC)
≥99% at Full Load
Frequency Range
40 to 70Hz at Full Load
Input Plug Type (Cord Length)
Hardwire w/optional NEMA L6-30P (6-ft.)
Input Surge Protection
Resettable Circuit Breaker
Maximum Input Current
38 Amps
Surge Joule Rating
3,140 Joules 
Output (AC Normal)
Voltage Range
208VAC (Default), 220, 230, 240VAC / 120VAC (Default), 110, 115VAC
Voltage Regulation
110,115,120,208,220,230,240VAC (±2%)
Frequency Range
50/60Hz, auto selecting, ±3Hz (unless synchronized to utility)
Efficiency (AC-AC)
93% at full-rated non-linear load
Output (Battery)
Output Waveform (Battery Mode)
True Sine-wave
Nominal Voltages
208VAC (Default), 220, 230, 240VAC / 120VAC (Default), 110, 115VAC
Voltage Regulation
Nominal +/-0.1% (until Low Battery warning)
Frequency Range
50/60Hz, +/-0.1Hz
Voltage T.H.D.
≤2% (Linear Load)
Overload Capacity
≥106% - ≤110% for 10 minutes / ≥111% - ≤125% for 5 minutes / ≥126% - ≤150% for 30 seconds
Batteries
Replacement Module
BM0097
Tool-less Replacement
Yes (Front panel replacement)
Runtime (Full/Half Load)
2 min. / 7 min.
Ind. Battery Bypass
Yes
DC Startup
Yes
Hot-swappable Batteries
Yes
Display & Communications
Front Panel Display
Multi-color, Touchscreen LCD
Alarm Silencer
Yes
Shutdown Software
SentryHD (available via download)
Communication Port(s)
USB/RS232 (Simultaneous access)
Comm. Cables Included
Yes
Remote Emergency Power Off Port
Yes
Environmental
Operating Temperature Range
'+32° to +104°F  (0° to +40°C)
Storage Temperature Range
'+5° to +131°F  (-15° to +55°C)
Operating (Storage) Humidity Range
0 to 95%, non-condensing
Operating Elevation
0 to +15,000 ft. (0 to +3,000m) 
Storage Elevation
0 to +50,000 ft. (0 to +15,000m)
Physical
Unit Dimensions (L x W x H)
23.82" x 17.24" 10.22" (605*438*260 mm)
23.82" x 17.24" 10.22" (605*438*173 mm)
23.82" x 17.24" 13.63" (605*438*346 mm)
Shipping Dimensions (L x W x H)
36.0" x 36.0" x 28.3" (702*550*285 mm)
36.0" x 36.0" x 28.3" (702*550*285 mm)
36.0" x 36.0" x 37.8" (915*915*961 mm)
Unit Weight
210.48 lbs. (95.5 Kgs.)
243.54 lbs. (110.5 Kgs.)
331.7 lbs. (150.5 Kgs.)
Shipping Weight
262.0 lbs. (118.9 Kgs.)
295.0 lbs. (133.8 Kgs.)
364.0 lbs. (165.2 Kgs.)
Warranty & Certifications
Standard Warranty
3 Years (Electronics and Batteries)
Connected Equipment Guarantee
$250,000
Safety Agency Approvals
cUL, CE,
Certifications
UL1778, FCC Class B, Energy Star 2.0, RoHS2

Endeavor 8kVA and Transformers

UPS Model
ED8KRT-3KTF
ED8KRT-5KTF
ED8KRT-6KTF2
ED8KRT-8KTF2
General Features
Topology
Double-conversion, Online
Number of Phases
Single (1ф 2W + G)
VA Rating
8,000VA
Load Capacity
7,065 Watts
6,975 Watts
6,930 Watts
6,840 Watts
Output Receptacles (208-240VAC)
(3) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
(3) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
(2) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
(2) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
Output Receptacles (120VAC)
(8) 5-15/20R
(4) 5-15/20R / (2) L5-30R / (1) 3-wire Terminal Block
(16) 5-15/20R
(12) 5-15/20R / (2) L5-30R / (1) 3-wire Terminal Block
Installation Format(s)
Rack or Tower
Input
Nominal Voltages
208 (Default), 220, 230, 240VAC
Acceptable Input Voltage
0 - 300VAC
Voltage Range
180-280VAC
Power Factor Correction (PFC)
≥99% at Full Load
Frequency Range
40 to 70Hz at Full Load
Input Plug Type (Cord Length)
Hardwire only
Input Surge Protection
Resettable Circuit Breaker
Maximum Input Current
51 Amps
Surge Joule Rating
3,140 Joules 
Output (AC Normal)
Voltage Range
 208 (Default), 220, 230, 240VAC / 120VAC (Default), 110, 115VAC
Voltage Regulation
110,115,120,208,220,230,240VAC (±2%)
Frequency Range
50/60Hz, auto selecting, ±3Hz (unless synchronized to utility)
Efficiency (AC-AC)
93% at full-rated non-linear load
Output (Battery)
Output Waveform (Battery Mode)
True Sine-wave
Nominal Voltages
 208 (Default), 220, 230, 240VAC / 120VAC (Default), 110, 115VAC
Voltage Regulation
Nominal +/-0.1% (until Low Battery warning)
Frequency Range
50/60Hz, +/-0.1Hz
Voltage T.H.D.
≤2% (Linear Load)
Overload Capacity
≥106% - ≤110% for 10 minutes / ≥111% - ≤125% for 5 minutes / ≥126% - ≤150% for 30 seconds
Batteries
Replacement Module
BM0098
Tool-less Replacement
Yes (Front panel replacement)
Runtime (Full/Half Load)
3 min. / 11 min.
Ind. Battery Bypass
Yes
DC Startup
Yes
Hot-swappable Batteries
Yes
Display & Communications
Front Panel Display
Multi-color, Touchscreen LCD
Alarm Silencer
Yes
Shutdown Software
SentryHD (available via download)
Communication Port(s)
USB/RS232 (Simultaneous access)
Comm. Cables Included
Yes
Remote Emergency Power Off Port
Yes
Environmental
Operating Temperature Range
'+32° to +104°F  (0° to +40°C)
Storage Temperature Range
'+5° to +131°F  (-15° to +55°C)
Operating (Storage) Humidity Range
0 to 95%, non-condensing
Operating Elevation
0 to +15,000 ft. (0 to +3,000m)
Storage Elevation
0 to +50,000 ft. (0 to +15,000m)
Physical
Unit Dimensions (L x W x H)
28.74" x 17.24" x 11.95" (730*438*303.5 mm)
28.74" x 17.24" x 11.95" (730*438*303.5 mm)
28.74" x 17.24" x 15.36" (730*438*390.0 mm)
28.74" x 17.24" x 15.36" (730*438*390.0 mm)
Shipping Dimensions (L x W x H)
36.0" x 36.0" x 30.1" (915*915*765 mm)
36.0" x 36.0" x 30.1" (915*915*765 mm)
48.0" x 40.0" x 39.6" (1220*1016*1006 mm)
48.0" x 40.0" x 39.6" (1220*1016*1006 mm)
Unit Weight
258.97 lbs. (117.5 Kgs.)
292.03 lbs. (132.5 Kgs.)
347.13 lbs. (157.5 Kgs.)
380.19 lbs. (172.5 Kgs.)
Shipping Weight
311.0 lbs. (141.1 Kgs.)
344.0 lbs. (156.1 Kgs.)
430.0 lbs. (195.1 Kgs.)
463.0 lbs. (210.1 Kgs.)
Warranty & Certifications
Standard Warranty
3 Years (Electronics and Batteries)
Connected Equipment Guarantee
$250,000
Safety Agency Approvals
cUL, CE
Certifications
UL1778, FCC Class B, Energy Star 2.0, RoHS2

Endeavor 10kVA and Transformers

UPS Model
ED10KRT-3KTF
ED10KRT-5KTF
ED10KRT-6KTF2
ED10KRT-8KTF2
ED10KRT-10KTF2
General Features
Topology
Double-conversion, Online
Number of Phases
Single (1ф 2W + G)
VA Rating
10,000VA
Load Capacity
8,865 Watts
8,775 Watts
8,730 Watts
8,730 Watts
8,550 Watts
Output Receptacles (208-240VAC)
(3) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
(3) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
(2) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
(2) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
(2) L6-30R / (2) L6-20R / (1) 3-wire Terminal Block
Output Receptacles (120VAC)
(8) 5-15/20R
(4) 5-15/20R / (2) L5-30R / (1) 3-wire Terminal Block
(16) 5-15/20R
(12) 5-15/20R / (2) L5-30R / (1) 3-wire Terminal Block
(8) 5-15/20R / (4) L5-30R / (2) 3-wire Terminal Block
Installation Format(s)
Rack or Tower
Input
Nominal Voltages
208 (Default), 220, 230, 240VAC
Acceptable Input Voltage
0 - 300VAC
Voltage Range
180-280VAC
Power Factor Correction (PFC)
≥99% at Full Load
Frequency Range
40 to 70Hz at Full Load
Input Plug Type (Cord Length)
Hardwire only
Input Surge Protection
Resettable Circuit Breaker
Maximum Input Current
63 Amps
Surge Joule Rating
3,140 Joules
Output (AC Normal)
Voltage Range
208 (Default), 220, 230, 240VAC / 120VAC (Default), 110, 115VAC
Voltage Regulation
110,115,120,208,220,230,240VAC (±2%)
Frequency Range
50/60Hz, auto selecting, ±3Hz (unless synchronized to utility)
Efficiency (AC-AC)
93% at full-rated non-linear load
Output (Battery)
Output Waveform (Battery Mode)
True Sine-wave
Nominal Voltages
208 (Default), 220, 230, 240VAC / 120VAC (Default), 110, 115VAC
Voltage Regulation
110, 115, 120, 208, 220, 230, 240VAC (±0.1%) (Until Low Battery warning)
Frequency Range
50/60Hz, +/-0.1Hz
Voltage T.H.D.
≤2% (Linear Load)
Overload Capacity
≥106% - ≤110% for 10 minutes / ≥111% - ≤125% for 5 minutes / ≥126% - ≤150% for 30 seconds
Batteries
Replacement Module
BM0098
Tool-less Replacement
Yes (Front panel replacement)
Runtime (Full/Half Load)
2 min. / 7 min
Ind. Battery Bypass
Yes
DC Startup
Yes
Hot-swappable Batteries
Yes
Display & Communications
Front Panel Display
Multi-color, Touchscreen LCD
Alarm Silencer
Yes
Shutdown Software
SentryHD (available via download)
Communication Port(s)
USB/RS232 (Simultaneous access)
Comm. Cables Included
Yes
Remote Emergency Power Off Port
Yes
Environmental
Operating Temperature Range
'+32° to +104°F  (0° to +40°C)
Storage Temperature Range
'+5° to +131°F  (-15° to +55°C)
Operating (Storage) Humidity Range
0 to 95%, non-condensing
Operating Elevation
0 to +15,000 ft. (0 to +3,000m)
Storage Elevation
0 to +50,000 ft. (0 to +15,000m)
Physical
Unit Dimensions (L x W x H)
28.74" x 17.24" x 11.95" (730*438*303.5 mm)
28.74" x 17.24" x 11.95" (730*438*303.5 mm)
28.74" x 17.24" x 15.36" (730*438*390.0 mm)
28.74" x 17.24" x 15.36" (730*438*390.0 mm)
28.74" x 17.24" x 15.36" (730*438*390.0 mm)
Shipping Dimensions (L x W x H)
36.0" x 36.0" x 30.1" (915*915*765 mm)
36.0" x 36.0" x 30.1" (915*915*765 mm)
48.0" x 40.0" x 39.6" (1220*1016*1006 mm)
48.0" x 40.0" x 39.6" (1220*1016*1006 mm)
48.0" x 40.0" x 39.6" (1220*1016*1006 mm)
Unit Weight
258.97 lbs. (117.5 Kgs.)
292.03 lbs. (132.5 Kgs.)
347.13 lbs. (157.5 Kgs.)
380.19 lbs. (172.5 Kgs.)
413.25 lbs. (187.5 Kgs.)
Shipping Weight
311.0 lbs. (141.1 Kgs.)
344.0 lbs. (156.1 Kgs.)
430.0 lbs. (195.1 Kgs.)
430.0 lbs. (195.1 Kgs.)
496.0 lbs. (225.0 Kgs.)
Warranty & Certifications
Standard Warranty
3 Years (Electronics and Batteries)
Connected Equipment Guarantee
$250,000
Safety Agency Approvals
cUL, CE
Certifications
UL1778, FCC Class B, Energy Star 2.0, RoHS2